06-24-2021, 03:12 PM
(06-24-2021, 02:39 PM)EricU Wrote: The easiest way to get the cable from one end of the house to the other is through the chase they made when they put a soffit around the I beam that holds up the house. It seems like if I just run it down that chase, it will be protected and supported. Anyone want to speculate if they will make me fasten it to the I beam? I think it wouldn't be much of a problem to cut into the drywall periodically and clamp it to the web of the beam, but I don't know that I see a reason to do that.
I'm not sure if they blocked it, so I might try running my fish tape down the beam
It's common to snake cabling, and uncommon to have to support and guard it. It's up to the code authority in the end, so I would probably ask first, but it's likely you can snake it along the beam and just leave it at that, supporting it wherever it's actually exposed.
300.4 Protection Against Physical Damage
(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (11⁄4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1⁄16 in.) thick.
Exception No. 1: Steel plates, sleeves, or the equivalent
shall not be required to protect rigid metal conduit, intermediate
metal conduit, rigid nonmetallic conduit, or electrical
metallic tubing.
Exception No. 2: For concealed work in finished buildings,
or finished panels for prefabricated buildings where
such supporting is impracticable, it shall be permissible to
fish the cables between access points.
Tom